We have come across an issue where we need to connect two 132/11kV power transformer LV (11kV) bus bars in parallel through an interconnector. The vector group of both is YN0yn0 however the HV bushing of one of the transformers is connected as Red phase to C Bushing, Yellow Phase to B Bushing and Blue Phase to A bushing of the transformer. Red, Yellow and Blue are network or system phases whereas A, B and C are transformer HV bushings. LV Connections are a, b, c following the HV A, B, C which means on LV side c will be red, b will be yellow and a will be blue. Now the other transformer has different configuration i.e on HV side Red to A, Yellow to B and Blue to C which means on LV side a is Red, b is Yellow and c is Blue. When the transformers are run independently this is fine however if one of the transformers is out of service and the LV bus bars are interconnected, the phasing will be different. We can’t change the HV phasing due to site constraints. We can change the LV cable connections so the question is will this solve the problem? I have attached a diagram as well. Your help is much appreciated.