Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Two-phase relief. API 520 vs ISO 4126-10 1

Status
Not open for further replies.

shvet

Petroleum
Aug 14, 2015
681
Good day, forum

I have an issue concerning backpressure (pardon my assumption concerning discharge coefficient).

API 520-1-2014 stated in equations C.43 and C.44 that mass flux is calculated with upstream pressure and backpressure difference or backpressure ratio. By this way backpressure affects PRV reqired capacity.

ISO 4126-10-2010 stated in equations 35 that mass flux mass flux is calculated with only upstream pressure. By this way backpressure does not affect PRV required capacity.

In case of high back pressure ratio this situation leads to required capacity calculated with API 520-1-2014 is much less than ISO 4126-10-2010. Can anyone comment this?
 
Replies continue below

Recommended for you

Right. My take on this is the following. PS: I do hope that some other well informed contributors confirm or otherwise.

API Is a user standard and has always included sizing factors contributing/affecting fluid flow. While the subject of back pressure correction factors would take an age to agree between everybody, API has established some compromised factors which should be considered in sizing. At its most basic, back pressure does affect sizing (factors less than 1.0 increase calculated area to compensate).

ISO-4126-10 Is a fairly new, but very comprehensive standard. Without reading it all, it appears that it concentrates more of the methodology of calculation without correction factors of any kind. In much the same way as the ASME NB-18 Book publishes base flow formulae without any correction factors.

Whatever method is used to determine a back pressure correction fator, the factor should be applied to any sizing calculation. Note that manufacturers should have their own determined correction factors. This as I understand, is still an ongoing thing within ISO-4126 (Part 8 ? - anyone ?) regarding flow testing as no one can agree the method.

Hope that helps in the interim and I await other comments.

Per ISO, only the term Safety Valve is used regardless of application or design.
 
Equation 35 in ISO 4126-10 includes the backpressure as part of the m[sub]ideal[/sub] term as p[sub]seat[/sub] from equation 32. It is not as explicitly stated as in the API documents. From the variable definitions following equation 34:

"p[sub]seat[/sub] is the pressure in the seat cross-section of the safety valve, expressed in pascals

If a critical pressure ratio has been established in the valve, the pressure, p[sub]seat[/sub], in the narrowest cross-section is equal to the critical pressure, p[sub]crit[/sub]. Otherwise, it equals the back pressure, p[sub]b[/sub]."

Note that p[sub]crit[/sub] is the fluid-dynamic critical pressure and not the same as p[sub]c[/sub], which is the thermodynamic critical pressure.

Bear in mind that API 520 Pt I equations C.43 & 44 are for subcooled liquids so the dP term uses either the backpressure or the saturation pressure because the fluid will choke at the phase boundary in the nozzle.

Hope this helps.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor