We’re thinking in taking advantage of an already constructed underground raceway (duct bank) of roughly 1 km (0.625 miles), with 4” ducts build in polyvinyl chloride (PVC), for installing a new medium-voltage circuit (13.8kV) of 5 conductors per phase of 500kcmil in size with feeder configuration 1/C. Three single phases are not allowed to fit in a 4 in duct (in compliance with NEC specifications), only two phases would fit, so we then would have to install phases R and S in one duct, phases S and T in the next duct, and successively. Also, two cables of the same phase should be fitted in one single duct. Otherwise, a new underground raceway with 6 in ducts should be constructed, but this is bounded due to economical constraints.
Using the actual configuration with two cables by duct, we would have higher magnetic fields because phases R, S and T are not longer together and magnetic field cancellation will no longer be achieved. Despite the non-metallic underground raceway, we would like to know if there are any important thermal effects in cables jackets that could have a immediate effect in the normal operation of the system, or any other side effect that could arise because of the use of this non-conventional configuration.
Thanks in advance for the help and analysis in this issue.
Sincerely,
Salvador Martínez
Using the actual configuration with two cables by duct, we would have higher magnetic fields because phases R, S and T are not longer together and magnetic field cancellation will no longer be achieved. Despite the non-metallic underground raceway, we would like to know if there are any important thermal effects in cables jackets that could have a immediate effect in the normal operation of the system, or any other side effect that could arise because of the use of this non-conventional configuration.
Thanks in advance for the help and analysis in this issue.
Sincerely,
Salvador Martínez