Ryan H
Structural
- Sep 3, 2021
- 27
I have a proposed 7ft wide basement window condition in an existing 8" masonry wall. I am told the tributary first floor load is 6ft and there's 8ft tall first floor block wall above this proposed opening. without looking too deep into it, I assumed the 8"x8" x 7ft precast lintel wouldn't work, no arching action. the arch suggested framing out the opening with 2x6 pressure treated for window attachment and using the middle mullion as load bearing for a midspan support. Is it possible to design a masonry lintel as two-span cont.? I know there will be negative moment over the center span. I also would need to check the Fv of the 2x6 p.t. nailer as well as the proposed (2)2x6 mullion. Just wanted to hear the thoughts on this proposed idea.