SprinklerDesigner2
Mechanical
- Nov 30, 2006
- 1,244
The engineer of record is telling me we have a two hour floor assembly separating the non-sprinklered first floor mercantile occupancy with tenants on the second floor apartments.
There are no plans to provide sprinklers in the mercantile occupancies and it just didn't feel right with me so I asked again to cover my rear end.
The response was:
The supply pipe is run in the non-sprinkled mercantile space and it appears it will be run exposed. Seems strange but the email, from the engineer of record through the architect, is my get out of jail free card but I am still curious and wondering if any of you ever run into something like this before?
There are no plans to provide sprinklers in the mercantile occupancies and it just didn't feel right with me so I asked again to cover my rear end.
The response was:
Engineer of Record said:In response to question 1, we are not sprinkling the first floor so his beam concerns at first floor framing are not applicable. We envision fire sprinkler riser in the riser room with piping at the underside of the 2-hour rated horizontal assembly then risers up the chases between the corridor closets at second floor to serve second floor residential units.
The supply pipe is run in the non-sprinkled mercantile space and it appears it will be run exposed. Seems strange but the email, from the engineer of record through the architect, is my get out of jail free card but I am still curious and wondering if any of you ever run into something like this before?