Hi folks, I go again with a long one.
I have a high rise building with a combined system. With two risers fed by a pump at the basement,please see attached drawing.
I´ve come across with this question previously but I see it needed a diagram and an update, so here I go again with this matter that is giving me some headaches.We are supposed to follow NFPA 101 and this is a high rise office building.
My company is buying this building under construction and they want to know if the fire system is ok, so they are asking my criteria on several points. I have my thoughts, but I´d like to hear your comments.
The risers are interconnected on each floor, with identical arrays on each side, they use 4" pressure reducing valves (Wilkins Zurn ZW109FP) this valves isolate the interconnection from the feeders and controls pressure for both sprinklers and hoses.
Question 1. Two flow alarms.
As there are flow detectors at both supplies on each floor, is this Ok?. I mean, when a sprinkler opens, you don´t know which one of the two flow sensors opens, or it may sense half the flow on each sensor, or it may not activate the detector due to the low flow (???).
I see that the alarm panel actually sound with the test device, but you only know it was on a floor but you don´t know if from the west o east side of the floor. The builder states that when opening the test connection on the test device located at the riser, it works, and that is all.
Quetion 2. Reated to the previous. Is it required to install a test connection at each side of the building on each floor. The builder says that he will install a test connection on the most hydraulic remote point at the highest floor and that is all.
Question 3.Check valves on sprinkler risers.
I´m not sure if per NFPA 24 it is required to install checks to prevent circulation. There are no check valves but the Wilkins pressure reducing valves. Do you know if the pressure reducing valves can be considered as check valves to prevent circulation (counter flow on the valve) or riser to get emptied on tests? Or is it required to install additional checks?.
Question 4. Pressure reducing valve flow range.
They decided to install the pressure reducing valve due to the local requirement of 85psi max for hoses, but they connected it so it also reduces pressure for both hoses and sprinklers (no real need, but the designer comments it works as an extra security to avoid unnecessarily high pressure on sprinklers).
Since the pressure reducing valve is 4" it is supposed that it has a limited working flow range (non pulsating), and I doubt it will work fine for the flow of one sprinkler. Is it Ok to use a pressure reducing valve like this for sprinklers? I mean how do you know it will work fine if one or two sprinklers open. Am I worrying for something that is not an issue for other reason?
Other valve manufacturers state that a 4" pressure reducing valve will work fine for a flow range from 70 to 300 gpms for example, and if you need lower flows, you will need a smaller valve installed on parallel, that goes down to the little flow. Wilkins data sheet does not mentions a lower limit, just an advivce on low velocities and consulting their experts (they havent answered yet).
The designer states that the design is OK, but the people buying the building is afraid to meet problems later if there is a code problem or bad design. Our local AHJ does not give a strong opinion on this design matters, and I want to give a good advice on this if possible.
Any input is highly appreciated.
I have a high rise building with a combined system. With two risers fed by a pump at the basement,please see attached drawing.
I´ve come across with this question previously but I see it needed a diagram and an update, so here I go again with this matter that is giving me some headaches.We are supposed to follow NFPA 101 and this is a high rise office building.
My company is buying this building under construction and they want to know if the fire system is ok, so they are asking my criteria on several points. I have my thoughts, but I´d like to hear your comments.
The risers are interconnected on each floor, with identical arrays on each side, they use 4" pressure reducing valves (Wilkins Zurn ZW109FP) this valves isolate the interconnection from the feeders and controls pressure for both sprinklers and hoses.
Question 1. Two flow alarms.
As there are flow detectors at both supplies on each floor, is this Ok?. I mean, when a sprinkler opens, you don´t know which one of the two flow sensors opens, or it may sense half the flow on each sensor, or it may not activate the detector due to the low flow (???).
I see that the alarm panel actually sound with the test device, but you only know it was on a floor but you don´t know if from the west o east side of the floor. The builder states that when opening the test connection on the test device located at the riser, it works, and that is all.
Quetion 2. Reated to the previous. Is it required to install a test connection at each side of the building on each floor. The builder says that he will install a test connection on the most hydraulic remote point at the highest floor and that is all.
Question 3.Check valves on sprinkler risers.
I´m not sure if per NFPA 24 it is required to install checks to prevent circulation. There are no check valves but the Wilkins pressure reducing valves. Do you know if the pressure reducing valves can be considered as check valves to prevent circulation (counter flow on the valve) or riser to get emptied on tests? Or is it required to install additional checks?.
Question 4. Pressure reducing valve flow range.
They decided to install the pressure reducing valve due to the local requirement of 85psi max for hoses, but they connected it so it also reduces pressure for both hoses and sprinklers (no real need, but the designer comments it works as an extra security to avoid unnecessarily high pressure on sprinklers).
Since the pressure reducing valve is 4" it is supposed that it has a limited working flow range (non pulsating), and I doubt it will work fine for the flow of one sprinkler. Is it Ok to use a pressure reducing valve like this for sprinklers? I mean how do you know it will work fine if one or two sprinklers open. Am I worrying for something that is not an issue for other reason?
Other valve manufacturers state that a 4" pressure reducing valve will work fine for a flow range from 70 to 300 gpms for example, and if you need lower flows, you will need a smaller valve installed on parallel, that goes down to the little flow. Wilkins data sheet does not mentions a lower limit, just an advivce on low velocities and consulting their experts (they havent answered yet).
The designer states that the design is OK, but the people buying the building is afraid to meet problems later if there is a code problem or bad design. Our local AHJ does not give a strong opinion on this design matters, and I want to give a good advice on this if possible.
Any input is highly appreciated.