cyriousn
Electrical
- Jul 19, 2017
- 23
We have a 325MW renewable site that was studied with a Y-g 345kv / Delta 34.5kv 350MVA two winding transformer but we are kicking around the idea of changing it to a three winding transformer to reduce the secondary current. If we kept the impedance the same between the primary and the two secondary windings wouldn't this essentially be the same transformer from a studies standpoint?
Also, I would assume it would be easier to manage the secondary cable connections if there was two secondary windings. The design currently calls for (4) MV switchgear lineups.
Also, I would assume it would be easier to manage the secondary cable connections if there was two secondary windings. The design currently calls for (4) MV switchgear lineups.