Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

Tx zero sequence

Status
Not open for further replies.

BJ-Elect

Electrical
May 13, 2024
2
0
0
GB
Hi,
For a standard Dy11 11/0.4kV UK Distribution Tx, with neutral solid earth.
What is the typical value for the zero sequence impedance Z0?.
Is it generally taken aws 1 x Pos sequence?.
links to standards/docs/literature etc. appreciated.
Any help appreciated.
Regards,
BJ
 
Replies continue below

Recommended for you

Absent zero sequence test data, for a 3-phase core type transformer assuming R0=R1 and X0=0.85*X1 seems to give reasonable results. For shell type transformers and banks of three 1-phase transformers assume Z0=Z1.

When one this sentence into the German to translate wanted, would one the fact exploit, that the word order and the punctuation already with the German conventions agree.

-- Douglas Hofstadter, Jan 1982
 
It is very interesting, indeed, prc. Mainly in- IEC 60076-8 - chapter 4 Zero-sequence properties – neutral load current and earth fault conditions, magnetic saturation, and inrush current. However, there is no useful data for a calculation.
 
Status
Not open for further replies.
Back
Top