Could someone, please tell me can a fire pump be UL/FM approved with the mechanical seal or it has to be with packing?

Thank you in advance!
 
Replies continue below

Recommended for you

Depends on the type of pump. If it is a centrifugal pump NFPA 20 has no requirements on the type of seal. If it is a positive displacement pump, NFPA 20 prohibits the use of packing and only permits either a mechanical or a lip seal.
 
Thank you Stookeyfpe!

The pump is a centrifugal horizontal split case, running at 1800RPM with an electrical motor, so if I understood it correct, it could be with a mechanical seal and UL/FM approved, right?
 