With a wood shear wall
(wood 2x studs with sheathing on one side - built-up end posts each end - hold downs at the end posts with bolts into the concrete foundation)
one has to use magnified seismic loads to design the hold down bolt to the concrete.
This usually requires either an Ω factor on the loads or "the maximum force that can be delivered to the system".
If the Ω results in too large forces to design to - and you want to somehow derive a weak link somewhere that would represent the maximum force delivered to the system, you might find one of these that would control:
1. Max. ultimate diaphragm shear into the shear wall.
2. Max. ultimate shear wall sheathing shear capacity
3. Max. ultimate end post tension capacity.
4. Max. ultimate end post compression capacity
5. Max. ultimate shear of anchor bolts along the base of the shear wall - either wood sill bearing failure or anchor failure
6. Max. overturning moment that the footings can take.
Most of these involve the "maximum ultimate" capacity of a wood entity. The NDS and other wood publications don't seem to provide that value. The safety factor or ultimate state of wood members is never directly given. We are given Fb, Ft, etc. but with no knowledge of the integrated variability in "failure" capacity.
Anyone have any thoughts on this?
With steel, we are required to use an Ry factor to account for the "true" yield level of the steel.
With wood, we don't know what sort of integrated increase value is applicable to wood.