We recently overhauled & tested a 600 HP slipring motor with following nameplate:
Output - 600 HP Speed - 990 RPM (50 Hz)
Stator Volts - 3300 V Rotor Volts - 720 V
Stator Current - 96 A Rotor Current - 390 A
During open shaft run, with the rotor energized at 400 V, we found unbalanced and hunting rotor currents of 70-75, 85-95 and 44-46 Amps. Suspecting rotor winding problem, I did a surge comparison test but it did not reveal any rotor winding problem (no phase unbalance or reversed connections etc.)
On open shaft run with stator energized at 400 V, the stator currents were equal and steady at 5.5 Amps.
The open shaft start up with stator energized was quicker and smoother as compared to start up with rotor energized (when it should have been the other way about) thus confirming that the unbalanced rotor currents were producing negative sequence torque resulting in net lower starting torque when rotor is energized.
Apparently both the stator & rotor were rewound some 12 years back and it was running without any problem. The motor came to me for conversion of sleeve bearings to anti-friction type.
What could cause these unbalanced and swinging rotor currents ? If the rotor winding is wrongly connected (reversed connections or unbalanced winding etc.) should not the surge test reveal it ?
I welcome any opinions on this strange phenomenon.
Output - 600 HP Speed - 990 RPM (50 Hz)
Stator Volts - 3300 V Rotor Volts - 720 V
Stator Current - 96 A Rotor Current - 390 A
During open shaft run, with the rotor energized at 400 V, we found unbalanced and hunting rotor currents of 70-75, 85-95 and 44-46 Amps. Suspecting rotor winding problem, I did a surge comparison test but it did not reveal any rotor winding problem (no phase unbalance or reversed connections etc.)
On open shaft run with stator energized at 400 V, the stator currents were equal and steady at 5.5 Amps.
The open shaft start up with stator energized was quicker and smoother as compared to start up with rotor energized (when it should have been the other way about) thus confirming that the unbalanced rotor currents were producing negative sequence torque resulting in net lower starting torque when rotor is energized.
Apparently both the stator & rotor were rewound some 12 years back and it was running without any problem. The motor came to me for conversion of sleeve bearings to anti-friction type.
What could cause these unbalanced and swinging rotor currents ? If the rotor winding is wrongly connected (reversed connections or unbalanced winding etc.) should not the surge test reveal it ?
I welcome any opinions on this strange phenomenon.