Unbalanced Snow Load IBC 2000 2

Status
Not open for further replies.

cmrazik

Structural
May 18, 2005
8
I am designing roof rafters for a single family residence. If I apply an unbalanced snow load, the rafters in the IBC Residential Code tables do not work. (My model includes a ceiling joist). I can only get the rafters in the table to work with balanced snow loads.

Does anybody know of a stipulation in the Code where you do not have to apply unbalanced snow loads to residential buildings?

Thanks!
 
Replies continue below

Recommended for you

So why dont you design with an unbalanced snow load.
 
I don't want to design the roof for unbalanced snow load if I don't have to. I was already accused by another engineer of being overconservative with the roof design on a previous residential design project. I would like to know definatively either way.
 
The leeward drifts from the ASCE 7 hammer a rafter design with 150% Pf. As I understand it, this is what the IBC says to do irrespective of occupany (I=1.0).

You are governed by the IRC. The IBC is a code book whereas I view the IRC as more of a recipe book. I am doing good to stay up with the IBC changes every three years and thus do not profess to know that much about the IRC. Look in the IRC and I expect it says the span tables are OK w/o drifting. IRC R301.2.3.

For what it's worth, I design any rafter and its connections for the drifted snow condition.

 
Check whether IBC and ASCE 7 even govern this design. Usually, the IRC controls residential design and you may not have to even refer to the other two.
 
If it is single family with 3 stories or less, then IRC is your code. If your ground snow load is 70 psf or less, you use the tables in IRC (chap 5,6 and 8). I don't have the commentary handy, but I think your issue is taken into account in the table values.

ZCP
 