acb324
Mechanical
- Aug 15, 2012
- 39
In a dormitory, can the dorm rooms be under negative pressure relative to the corridor? Does this create a potential issue if a fire started in one of the dorm rooms, as far smoke pouring out into the egress corridor?
As far as I can tell, NFPA 101 chapter 28 on dormitories prohibits transoms, louvers, or transfer grilles, but does not speak to the air transfer through the undercut of a door.
NFPA 80 allows up to 3/4" of undercut on a fire rated door.
My confusion really arises from NFPA 90A. 4.3.12.1.3.2 regarding egress corridors states that where door clearances do not exceed those specified for fire doors in NFPA 80, air transfer caused by pressure differentials shall be permitted. However, immediately after that 4.3.12.2 states that exit passageways shall not be used as a part of a supply, return, or exhaust system serving other areas of the building. It seems to me that an egress corridor is an exit passageway, and so these two things directly contradict one another. Any clarification on the intent here would be helpful. Thank you.
As far as I can tell, NFPA 101 chapter 28 on dormitories prohibits transoms, louvers, or transfer grilles, but does not speak to the air transfer through the undercut of a door.
NFPA 80 allows up to 3/4" of undercut on a fire rated door.
My confusion really arises from NFPA 90A. 4.3.12.1.3.2 regarding egress corridors states that where door clearances do not exceed those specified for fire doors in NFPA 80, air transfer caused by pressure differentials shall be permitted. However, immediately after that 4.3.12.2 states that exit passageways shall not be used as a part of a supply, return, or exhaust system serving other areas of the building. It seems to me that an egress corridor is an exit passageway, and so these two things directly contradict one another. Any clarification on the intent here would be helpful. Thank you.