Since the copper wire from a cable presents the maximum expansion factor of about 17 mm per 1km and 1 grade C, and if the installation temperature is -20oC and the coldest ambient temperature is -40oC then the retraction of the cable will be 340 mm and if the installation temperature was +40oC the retraction length will be 1360 mm per 1 km.
The same in dilatation case if the installation temperature was -20oC and the normal temperature of the conductor will be 90oC then the cable will expand 1870 mm per 1 km. In short circuit case if the copper conductor temperature reach 250 oC the expansion length will be then 4.6 m.
The insulation and jacket expansion factor is 10-15 times higher but the expansion force is not enough to overcome the copper wire resistance and to produce another significant expansion.
.