Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Underground Duct Bank Ampacity Calculation

Status
Not open for further replies.

budhiman

Electrical
Jan 26, 2016
60
Hello All,

I will be using software (etap) for underground duct ampacity calculations. I was wondering what all information for cable is required to use Neher-Mcgrath equation. I will be requesting information for cables from the cable manufacture, want to make sure I request the correct items.
 
Replies continue below

Recommended for you

The NEC cable section used to show the Neher-Mcgrath equation and defines its parameters - however, in 30+ years I have yet to see an actual example of this formula used. For duct bank ampacity deration, etc, you will probably better off using the NEC figures and tables.
 
For low voltage cable [up to 2000 V rating] you need:
-conductor diameter[it could be different for class B stranded, compressed or compacted]
- insulation thickness[or insulated core diameter]
- jacket [if any] thickness or diameter
- it could be a nylon overjacket sometime.
For shielded cable [up to 35 kV] you'll need more. See-for instance:
Calculation of Underground Cable Ampacity by Francisco de Leon
 
Complex_cable_cross_section_xgkocg.jpg
 
ETap takes care of the conductor info for you, just tell it the size.

The more important info is the installation characteristics. rho of the surroundings, spacing between cables/ducts, load factor, current
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor