Designer_82
Mechanical
- Oct 17, 2020
- 58
I ran an underground ductbank ampacity calculation in ETAP.
Although the ductbank is very large with about 46 conduits, the calculation results are crippling.
It shows a 1200 Amp base ampacity cable derated to only about 400 Amps. A 67% derate.
We're already running 4 sets of 500Kcmil for 1200A feeders.
Are these ductbank ampacity calculations too conservative?
Any experience with this? Do these results seem reasonable?
Although the ductbank is very large with about 46 conduits, the calculation results are crippling.
It shows a 1200 Amp base ampacity cable derated to only about 400 Amps. A 67% derate.
We're already running 4 sets of 500Kcmil for 1200A feeders.
Are these ductbank ampacity calculations too conservative?
Any experience with this? Do these results seem reasonable?