NinerStruct
Structural
- Nov 5, 2012
- 36
I'm working on a project where we're putting an elevator in the corner of an existing brick building. The existing footings are not as deep as we had originally thought, based on what few existing drawings we had. So now it looks like we're going to have to underpin a portion of the existing walls.
On one side (north) of the elevator pit, the footing is ~4 ft higher than we were need for the pit, and on the adjacent side (east) the footing is ~1.5 ft higher. Below are section sketches of the elevator shaft.
The total length of underpinning is roughly 18-20 ft. I am planning on having them underpin in 4ft. sections, leaving a 3" gap between bottom of existing and top of underpinning, that is to be dry-packed with grout.
The existing footings also project about 4" into the elevator pit as well. I'm waiting to hear back from the architect on whether or not we have the clearance within the shaft to accommodate this, but if not, can the underpinning be poured as shown in the detail linked below, or does the lower portion need to be a separate pour?
I will likely tie the underpinning into the mat footing for the bottom of the pit, but should I provide any sort of reinforcing within the underpinning since it's retaining soil now?
On one side (north) of the elevator pit, the footing is ~4 ft higher than we were need for the pit, and on the adjacent side (east) the footing is ~1.5 ft higher. Below are section sketches of the elevator shaft.
The total length of underpinning is roughly 18-20 ft. I am planning on having them underpin in 4ft. sections, leaving a 3" gap between bottom of existing and top of underpinning, that is to be dry-packed with grout.
The existing footings also project about 4" into the elevator pit as well. I'm waiting to hear back from the architect on whether or not we have the clearance within the shaft to accommodate this, but if not, can the underpinning be poured as shown in the detail linked below, or does the lower portion need to be a separate pour?
I will likely tie the underpinning into the mat footing for the bottom of the pit, but should I provide any sort of reinforcing within the underpinning since it's retaining soil now?