robclay
Electrical
- Dec 1, 2004
- 5
I am not just a bit rusty, but majorly rusty...
I am using an AB 1756-L55 ControlLogix 5555 Controller.
It has a remote 1794AENT/A Adapter.
I have an Analog Input Module - 1794/IE8
I have an Analog Output Module - 1794/OE4
My Analog Input Module is configured for (0-10V) / (0-20mA)
My Analog Output Module is configured for 4-20mA
For Inputs: I have been told that a 4mA signal will produce a value of 6242 (I figure it is exactly 6241.6). And a 20mA signal will produce a value of 31208.
For Outputs: 0mA = 0 value, and 20mA - 30840.
1. Can someone confirm this?
2. Where did they find this? In the manual for the analog cards, the PLC?
3. I forced an output to 15420 and noticed that the output was not 12mA. Should it have been?
4. For a PID Loop, in RSLogix v11.15, I am setting up a PID loop and am looking at the scaling tab. I have a Pressure Transmitter that is ranged from 0-300psi. I have a Control Valve that opens from 0 to 100%.
Should my Values be:
Process Variable:
Unscaled Max = 31208
Unscaled Min = 6241.6
Engineering Unit Max = 300
Engineering Unit Min = 0
Control Variable:
Max at 100% = 30840
Min at 0% = 0
I am sure this is such basic stuff, I am just trying to gain a better understandning.
I am using an AB 1756-L55 ControlLogix 5555 Controller.
It has a remote 1794AENT/A Adapter.
I have an Analog Input Module - 1794/IE8
I have an Analog Output Module - 1794/OE4
My Analog Input Module is configured for (0-10V) / (0-20mA)
My Analog Output Module is configured for 4-20mA
For Inputs: I have been told that a 4mA signal will produce a value of 6242 (I figure it is exactly 6241.6). And a 20mA signal will produce a value of 31208.
For Outputs: 0mA = 0 value, and 20mA - 30840.
1. Can someone confirm this?
2. Where did they find this? In the manual for the analog cards, the PLC?
3. I forced an output to 15420 and noticed that the output was not 12mA. Should it have been?
4. For a PID Loop, in RSLogix v11.15, I am setting up a PID loop and am looking at the scaling tab. I have a Pressure Transmitter that is ranged from 0-300psi. I have a Control Valve that opens from 0 to 100%.
Should my Values be:
Process Variable:
Unscaled Max = 31208
Unscaled Min = 6241.6
Engineering Unit Max = 300
Engineering Unit Min = 0
Control Variable:
Max at 100% = 30840
Min at 0% = 0
I am sure this is such basic stuff, I am just trying to gain a better understandning.