sysengineer
Electrical
- Feb 16, 2012
- 56
I'm confused about short circuit currents and how they are used to determine the ratings of equipment within an electrical system.
My own intuition would suggest that that a system must be designed such that any equipment upstream of the short circuit must be able to withstand both the current and energy produced as a result for sufficient time for the protective device to interrupt.
So for example if a single phase feeder is supplying some sort of control panel and a short occurs on this cable everything upstream of this fault i.e. the dist. board or whatever must be able to withstand the fault conditions until the protective device interrupts.
On the other hand if the control panel is supplying some sort of external heater and a short occurs within the heater, everything upstream of the heater must be rated i.e. up to the protective device inside the control panel.
My reasoning is that if a short occurs within a supply system, (ignoring back emf from motors and such for now) everything downstream of the short will not be affected i.e. very little current will flow as the resistance path of the short circuit is tiny compared to that of the downstream load.
The confusion is that IEC 61439: Low Voltage Switchgear & Controlgear Assemblies states:
"6.2 Prospective short-circuit current at supply terminals Icp (kA)
The prospective short-circuit current is the current that would flow if the supply conductors to
the ASSEMBLY were short-circuited with negligible impedance at the supply terminals of the
ASSEMBLY."
If the supply conductors to an assembly are short circuited then in terms of the assembly what is the problem? Surely due to the negligible impedance of the short very little current would flow?
My own intuition would suggest that that a system must be designed such that any equipment upstream of the short circuit must be able to withstand both the current and energy produced as a result for sufficient time for the protective device to interrupt.
So for example if a single phase feeder is supplying some sort of control panel and a short occurs on this cable everything upstream of this fault i.e. the dist. board or whatever must be able to withstand the fault conditions until the protective device interrupts.
On the other hand if the control panel is supplying some sort of external heater and a short occurs within the heater, everything upstream of the heater must be rated i.e. up to the protective device inside the control panel.
My reasoning is that if a short occurs within a supply system, (ignoring back emf from motors and such for now) everything downstream of the short will not be affected i.e. very little current will flow as the resistance path of the short circuit is tiny compared to that of the downstream load.
The confusion is that IEC 61439: Low Voltage Switchgear & Controlgear Assemblies states:
"6.2 Prospective short-circuit current at supply terminals Icp (kA)
The prospective short-circuit current is the current that would flow if the supply conductors to
the ASSEMBLY were short-circuited with negligible impedance at the supply terminals of the
ASSEMBLY."
If the supply conductors to an assembly are short circuited then in terms of the assembly what is the problem? Surely due to the negligible impedance of the short very little current would flow?