Rectified
Electrical
- Oct 14, 2020
- 4
The installation is a new 22kW Generac natural gas-powered standby generator in the U.S. At initial startup, with no load connected, the frequency readout is both abnormal and unstable, rising to about 419 Hz. I get the same reading at the automatic transfer switch and the generator (with the output conductors disconnected). By its sound, the engine speed is stable and seems normal, and the voltage is normal and stable. Also note that the engine runs continuously with this condition -- no over-frequency shutdown. Could there be distortion, such as might be encountered on a variable speed motor drive, causing a false reading on my DMM?
The meter is a Klein CL700 digital multimeter, with only one auto-ranging frequency setting. I used it to test the utility and a portable generator (inverter type). Both came in stable at almost dead-on 60.00 Hz. I have not connected a load to the generator, because manufacturer instructions forbid doing so if the measured frequency is not normal. The labels claim the unit was tested at the factory. The factory tech support had never heard of such a problem.
The meter is a Klein CL700 digital multimeter, with only one auto-ranging frequency setting. I used it to test the utility and a portable generator (inverter type). Both came in stable at almost dead-on 60.00 Hz. I have not connected a load to the generator, because manufacturer instructions forbid doing so if the measured frequency is not normal. The labels claim the unit was tested at the factory. The factory tech support had never heard of such a problem.