Unsymmetrical generator load.

Status
Not open for further replies.

Audun

Electrical
Jun 4, 2002
14
Hi

What guidlines do you know regarding unsymmetrical threephase generator load.
My question relates to the following case:
480V diesel generator.
Load currents for phases are approx.
2000 A, 2800 A, 800 A

PF=0.8

What generator rating is recomended. I think there are som production standards regarding singlephase load that generator manufacturers should follow for a threephase gen.

Audun
 
Replies continue below

Recommended for you

The concern as you are probably aware is heating of the generator rotor surface. The negative sequence component of the current travels in the reverse direction creating 120hz current which will concentrate in the surface of the rotor and create heating.