Unusual Guardrail In-fill - Residential

XR250

Structural
Jan 30, 2013
5,305
I have been asked to evaluate some guardrail in-fill to determine if it meets the 50 PSF IRC requirement. The infill is 4" O.C. horizontal 1/4x1 1/2" flat bar (1 1/2" horizontal). spanning 4 ft between 4x4 treated posts.
Realistically, I know this will work fine but...

1) Seems like evaluating the 1/4" compression flange of the flat bar as un-braced over 4 ft. will be tough. Especially as any realistic load on it will be de-stabilizing.
Regardless, even if it is unstable, it will just end up acting as a catenary between posts so who cares?

2) Will the baby's head spread these apart? I can tighten up the spacing if needed.
 
Replies continue below

Recommended for you

The arch. has decided to move a different direction but this would be an interesting discussion regardless.
 
Our guardrails are required to be non-climbable. It sounds like they wanted to make a ladder.

That part being said, a quick back of napkin calc shows that a 1/4" flat bar should be good with those proportions. I get that works out to around 3.2 ksi bending stress, I can't imagine the unbraced length being that punishing on the allowable bending stress. Around here, even flat bar is 44 ksi yield.
 
The wind load would be not a problem. The kid or kid at heart will try and climb up infill like that. The bars would be bent after that.
 
Use Roarc for strength determination. I occasionally encounter this type of construction, but the BARs are vertical. The small BAR stock will likely deform plastically with time due to the limited thickness of the BAR.
 
The wind load would be not a problem. The kid or kid at heart will try and climb up infill like that. The bars would be bent after that.
Agreed. I don't think the code requirement of 50 psf is for wind - rather to keep someone from falling through it who has enough velocity.
It is a dumb design IMHO. Although, once kids try to climb a cable rail, it is usually loose after that.
 