electricpete
Electrical
- May 4, 2001
- 16,774
I have a Reliance motor 1970’s vintage 800HP 4KV.
The nameplate includes:
HP – “800”
RPM – “890”
Ins Class – “F”
Ins Type – “RPI”
Ambient – “40” C
Duty - “Cont”
“Max Rise WDG 60C”
The items in double-quotes are the items which are custom-stamped into the nameplate. For example HP is printed onto the nameplate for general use and “800” is stamped as a parameter unique to this motor.
If I saw Max Rise of 80C, I would conclude this is a motor specified to have class F insulation and design for a class B rise (40C ambient + 80C average rise + 10C hot-spot allowance). I don’t know how to interpret the “Max Rise WDG 60C”Max Rise 60C. I am sure this is something we would not have specified during purchase of the motor.
My question: What do you think is the meaning of “Max Rise WDG 60C”Max Rise 60C
If I were attempting to predict aging/reliability based upon actual loading and measured winding temperatures in-service, do I need to give any consideration to this statement “Max Rise WDG 60C”Max Rise 60C or can I simply consider it to be class F?
(I am not interested in any general/philocophical discussion of aging evaluation, only the role of this 60C rise should play in an evaluation)
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
The nameplate includes:
HP – “800”
RPM – “890”
Ins Class – “F”
Ins Type – “RPI”
Ambient – “40” C
Duty - “Cont”
“Max Rise WDG 60C”
The items in double-quotes are the items which are custom-stamped into the nameplate. For example HP is printed onto the nameplate for general use and “800” is stamped as a parameter unique to this motor.
If I saw Max Rise of 80C, I would conclude this is a motor specified to have class F insulation and design for a class B rise (40C ambient + 80C average rise + 10C hot-spot allowance). I don’t know how to interpret the “Max Rise WDG 60C”Max Rise 60C. I am sure this is something we would not have specified during purchase of the motor.
My question: What do you think is the meaning of “Max Rise WDG 60C”Max Rise 60C
If I were attempting to predict aging/reliability based upon actual loading and measured winding temperatures in-service, do I need to give any consideration to this statement “Max Rise WDG 60C”Max Rise 60C or can I simply consider it to be class F?
(I am not interested in any general/philocophical discussion of aging evaluation, only the role of this 60C rise should play in an evaluation)
=====================================