Hi,
I have a situation.
Added a large medium voltage (12.5 kV) switch enclosure to a generator circuit. Only available siting was between two large current-limiting reactors. The switch enclosure sits approx. 6 ft. from one reactor, approx. 12 ft. from the other. Before siting we considered that there may be some induction in the switch enclosure, but went ahead with the siting.
Now that the switch is in service, there is obvious inductive heating going on in the switch enclosure. It is present all over the enclosure, but is especially concentrated in two places (possibly where most of the bus work is inside the enclosure. This is a real problem when combined with solar temp. gain and high ambient temperatures.
What steps can I take to reduce the inductive heating in this switch enclosure (other than moving it)?
Are there barrier materials that will cut down the EM induction?
Note: The reactors are enclosed in vented metal enclosures, with steel side panels that are insulated to prevent large eddy currents.
Thanks,
Brian
I have a situation.
Added a large medium voltage (12.5 kV) switch enclosure to a generator circuit. Only available siting was between two large current-limiting reactors. The switch enclosure sits approx. 6 ft. from one reactor, approx. 12 ft. from the other. Before siting we considered that there may be some induction in the switch enclosure, but went ahead with the siting.
Now that the switch is in service, there is obvious inductive heating going on in the switch enclosure. It is present all over the enclosure, but is especially concentrated in two places (possibly where most of the bus work is inside the enclosure. This is a real problem when combined with solar temp. gain and high ambient temperatures.
What steps can I take to reduce the inductive heating in this switch enclosure (other than moving it)?
Are there barrier materials that will cut down the EM induction?
Note: The reactors are enclosed in vented metal enclosures, with steel side panels that are insulated to prevent large eddy currents.
Thanks,
Brian