zurch1818
Structural
- Feb 16, 2015
- 24
I'm currently in the process of analyzing a concrete foundation of a multi-leg water tower that was designed in the 1936. The plans have survived time and show a typical pad and pier foundation. The one thing that is odd to me is they call out rebar in the bottom pad, but all they show in the pier is the two anchor rods. I believe the pier has is plain and has no rebar in it. I'm hoping that they poured the pad and pier at the same time to prevent a cold joint, but I really don't know the order of how it was actually formed. As seen in the photo, the foundation has already showed some significant cracking in ways that make me believe there isn't any steel besides the anchor rod in the foundation.
When I turn to section 22.5.3 of ACI 318-08, it gives a way to calculate the bending capacity of plain concrete. However, with the loads I have, I don't really have much bending. It is concrete that has to support pure tension which seems weird to use the combined bending and axial compression equation. Does it still make sense to keep my stress under the the 5*sqrt(f'c) value or do I just have to fail the foundation because it doesn't have minimum temp/shrinkage steel in it?
Thanks for your opinion.
When I turn to section 22.5.3 of ACI 318-08, it gives a way to calculate the bending capacity of plain concrete. However, with the loads I have, I don't really have much bending. It is concrete that has to support pure tension which seems weird to use the combined bending and axial compression equation. Does it still make sense to keep my stress under the the 5*sqrt(f'c) value or do I just have to fail the foundation because it doesn't have minimum temp/shrinkage steel in it?