I would be interested to know how others handle the high earth loop impedance which is generally measured on UPS circuits.
The contractor who tested our office told me that they do not normally do EFLI tests on UPS circuits for fear of damaging said device. I insisted they were done.
In our office disconnection times would not be met on circuits fed by the UPS (15kVA unit). I have had a 300mA RCD installed on the output of the UPS and to date fortunately had no trips.