tranny
Electrical
- Jan 6, 2003
- 13
I have a UPS system in which the essential load is normally fed from the ups. I event of an overload or failure of the ups, a static switch will transfer the load to bypass. Bypass consists of a 480 to 120 v single phase constant voltage transformer. The essential bus that is fed from this transformer and the inverter consists of a 120 volt panel where there are two pole breakers being used. The line and neutral wires can be switched with the breaker. Is this normal??
Also, should the secondary of the constant voltage transformer be grounded anywhere? Right now, X1 and X2= 120V, X2 and X3= 120 volts and X1-X3= 240v. the only wires hooked up is x1 and x2. X3 is floating. if there was a fault on one of the secondaries, nothing would trip, right? Unless the other leg faulted, then there would be smoke, correct? Thank you
Also, should the secondary of the constant voltage transformer be grounded anywhere? Right now, X1 and X2= 120V, X2 and X3= 120 volts and X1-X3= 240v. the only wires hooked up is x1 and x2. X3 is floating. if there was a fault on one of the secondaries, nothing would trip, right? Unless the other leg faulted, then there would be smoke, correct? Thank you