rajendrarohra1978

Electrical
Jul 16, 2013
19
Hi!
I have a question regarding UPS loading, can common load be supplied by two independent UPS. The common load is instrument servers. I have a doubt about synchronization of UPS outputs. What if the supply for both UPS is connected at some point.

Thanks
 
Replies continue below

Recommended for you

The best way to do that is to have equipment with dual power supplies, that way the two UPS AC systems never interact but the critical equipment has both sources.
 