At an installation there is a 400v, 50Hz, 3 ph,4wire, DB with a Fault Level of 35kA. It is fed from a 1MVA, 11kV to 400v, DYn11 trf. This DB feeds a 40kVA, three phase, UPS device. In the Main DB the breaker feeding the UPS is a 125A thermal magnetic MCB set at the correct levels. No earth connected.
UPS feeds out with a 4 wire system but is not earthed. It feeds on a 100A breaker to a SDB. 25mm sq, 4 core, SWA, ECC, PVC, PVC. The SDB then feeds 9 Emergency Lighting DBs with 3 pole MCBs. Still no earth. These DBs feed a 3 ph, 4 wire lighting circuits from a 32A, 3 pole breaker. The cable is a 16mm sq four core. It feeds lights in a single circuit with different phased tapped of at each light (220v single phase) to balance the load. Question 1. What should the correct protection method be? 4 wire or 3 wire / pole breaker?
Question 2. What happens when luminaires start to fail and they are all happen to be on one phase but the breaker does not trip. The voltage on some phases will go up so why no earth?
Quesstion 3. With the first ground fault there is no path so no current. When the second ground fault happens will the 32A MCB trip? I say it depends where the fault is.
UPS feeds out with a 4 wire system but is not earthed. It feeds on a 100A breaker to a SDB. 25mm sq, 4 core, SWA, ECC, PVC, PVC. The SDB then feeds 9 Emergency Lighting DBs with 3 pole MCBs. Still no earth. These DBs feed a 3 ph, 4 wire lighting circuits from a 32A, 3 pole breaker. The cable is a 16mm sq four core. It feeds lights in a single circuit with different phased tapped of at each light (220v single phase) to balance the load. Question 1. What should the correct protection method be? 4 wire or 3 wire / pole breaker?
Question 2. What happens when luminaires start to fail and they are all happen to be on one phase but the breaker does not trip. The voltage on some phases will go up so why no earth?
Quesstion 3. With the first ground fault there is no path so no current. When the second ground fault happens will the 32A MCB trip? I say it depends where the fault is.