Universe_in_Flux
Electrical
- Oct 26, 2020
- 8
For one project, we have a requirement of 10kVA parallel redundant UPS with common bypass. Till now we have only purchased UPS which have static switches in bypass and inverter path. Recently one vendor has offered a UPS which has a static switch on bypass path, however they have provided contactor on inverter output side. our philosophy is to operate critical loads on UPS only, and switch to bypass only when there is any problem with UPS.
Technical specifications of offered model meets requirements of our specifications, however I am hesitant to go ahead with this topology of UPS since it is new to us. I am specifically worried about impact on availability of UPS, since failure of coil or actuating mechanism may lead to loss of load due to contactor failure on shorted position.
Do you have experience of using UPS which do not have inverter side static switch? If yes, Have you faced any reliability or operational issues with this? Could you please suggest a good reason to accept or reject this topology?
Technical specifications of offered model meets requirements of our specifications, however I am hesitant to go ahead with this topology of UPS since it is new to us. I am specifically worried about impact on availability of UPS, since failure of coil or actuating mechanism may lead to loss of load due to contactor failure on shorted position.
Do you have experience of using UPS which do not have inverter side static switch? If yes, Have you faced any reliability or operational issues with this? Could you please suggest a good reason to accept or reject this topology?