I'm a technician on a mission base in the Amazon. A few days ago we suffered a lighting strike to our electrical system when the generator was not running. The strike damaged one of our three step up transformers for our electrical distribution system. In a pinch could I run the generator only using two of it's three phases? Can I leave the third phase unloaded? I know people always say you can't but if you be sure to not exceed the rating of any one phase does it matter if the other phases are loaded or not?
The transformers are oil cooled 75KVA pole mountable units. The high voltage sides are wired delta, with the output like this:
trans1---------trans2
\ /
\ /
\ /
\ /
trans3
Also since we lost one transformer could I use just two transformers with the high voltage sides wired like this and just use two phases?:
---------------
trans1 trans2
---------------
Thanks!