Use of AI for learning and practicing structural design 3
strawhats2000
Industrial
Jan 23, 2012
32
Hi All,
I will like to get your feedback on the best AI tools or application with AI integrated that can be used to learn and practice Structural Detailing of Structural elements like Slab, Beam, Columns, Staircase, Foundation to BS or EN norms/codes in Reinforced Concrete. According with some preliminary chatting with an AI bot, I was told that Civils.ai, Autodesk Robot Structural Analysis Professional and Tekla Structural Designer does have BS8110 and AI integrated and does contain some comprehensive training materials. I will like to get your advice as to which software is more user-friendly and best for beginner with the less time consuming learning curve and adaptability. Perhaps bordering a high imagination, I was thinking of a program that can import an autocad layout, elevations and elevation and calculate loads, position column, beams etc and even calculate and detail rebars. Is that possible or near possible? Thanks.
how sure are you about the RH deflection ? It is a small force, so maybe deflection is being dominated by the main span ?
Yes that's right the slope from w1 at B dominates the slight change in slope caused by w2 outboard of B
% Given Data
E = 30000 * 1000; % psi (modulus of elasticity)
I = 104.3; % in^4 (moment of inertia)
w1 = 35 / 12; % lbf/in (uniform load on span 1)
w2 = 15 / 12; % lbf/in (uniform load on span 2)
L1 = 120; % in (span 1 length)
L2 = 48; % in (span 2 length)
BCs
Beam is simply supported at A x=0
Beam is simply supported at B x=L1
Tip is free at X=L1+L2
The solution is the superposition of 2 load cases, w1 and w2
Note I've forced BM at tip to be zero, this gives a slightly different curve. Sorry I'm getting this problem confused with another that uses the same script. There's really only 2 load cases w1 and w2, superimposed.
w1 only,
w2 only
and just to check the superimposed solution, with deflection at x= 10 ft forced to be zero
that looks about right the combined loading has less defection at the RH tip and at the mid-span than the main spin only loading.