rockman7892
Electrical
- Apr 7, 2008
- 1,156
With MVA rated (K>1) being a thing of the past more associated with older Switchgear and new current rated (K=1) being available for new Switchgear or breaker replacements why would anyone want to purchase/install MVA rated breakers for new Switchgear or breaker replacement in older Switchgear?
the reason I ask is that I notice that many of the major manufacturers still offer MVA rated breakers along with the newer K=1 rated breakers. Even when replacing breakers in existing switchgear I believe you can still replace the older breakers with newer K=1 rated breakers in the existing switchgear.
Are there any specific reasons or applications that would justify the use of an MVA rated breaker?