kedminster
Electrical
- Nov 21, 2009
- 16
I am working on a project where I need to isolate a 1500W, 1kV power supply with an electromechanical relay/contactor as part of a safety system to meet the requirements of IEC category 3. I need to switch the output (1kV) but not under load. The primary switching element(s) need to be monitored by aux contacts. I am using a Banner GM-FA-10J gate monitor safety module and appropriate switch to control the Banner module.
I am having a hard time finding a single relay with aux contacts that is rated for 1kV DC to do this. I am considering using 2 contactors in series (each rated 690VDC)to perform the isolation function. Is a series connection of monitored contacts an acceptable solution? If not, any suggestions on a source for DC relays/contactors rated 1kV or more that are not enormous. I only need 1.5A rated contacts and most parts I have found are 50A or more.
Thanks in advance for any feedback
I am having a hard time finding a single relay with aux contacts that is rated for 1kV DC to do this. I am considering using 2 contactors in series (each rated 690VDC)to perform the isolation function. Is a series connection of monitored contacts an acceptable solution? If not, any suggestions on a source for DC relays/contactors rated 1kV or more that are not enormous. I only need 1.5A rated contacts and most parts I have found are 50A or more.
Thanks in advance for any feedback