To answer your question, the IEEE 400.2-2013 standard for VLF testing MV and HV cable specifies the following for 5 kV and 15 kV shielded power cable of any solid dielectric material:
5 kV cable: Installation test voltage = 13 kV peak - phase to ground, Acceptance = 14 kV peak, Maintenance = 10 kV peak.
15 kV cable: Installation test voltage = 27 kV peak - phase to ground, Acceptance = 30 kV peak, Maintenance = 22 kV peak.
The above numbers assume the use of a sine wave producing VLF power supply operating at 0.1 Hz. This is a Voltage Withstand, pass/fail test. The test duration should be a minimum of 30 minutes with 60 minutes preferred. This standard also defines the test methods for performing a Tan Delta diagnostic test on the cable, where the VLF applies an over voltage of 1.5 - 2.0 times normal voltage and the TD, or loss factor, of the cable is measured, which provides an indication of the extent of insulation degradation. 50/60 Hz test voltage levels are lower and for shorter duration. Depending on the capacitance (length and size) of the cables to be tested, the current/power required from the test set may be prohibitively high, which is why power frequency is rarely used in the field and why VLF technology was developed and now used worldwide.
Hope this helps.