We are working on improving the ventilation to our factory. Our current dryer runs at a constant 45,000 cfm when it is running. I was looking at ducting this into our factory to act as 2 exhaust fans. Being a food grade plant, we maintain positive pressure of roughly .2" wg, to maintain this, we would be adding at the minimum 45,000 cfm of intake fans. My concerns on doing this is the exhaust fan is capable of 20" wg. To prevent this motor from sucking in our walls, I would be adding a pressure sensor to the factory to monitor the pressure. This would kick the dryer fan off if too much vacuum is sensed within the factory. To prevent the operators from running this fan in 'hand' mode, I would wire in a keyed switch to the MCC bucket. I would think I'd want to connect up the new intake fans to VFD's such that they ramp up with the dryer to maintain our pressure, also controlled by the pressure sensor. My other thought would be to wire each intake fan up to a different pressure sensor for redundancy sake.
Thoughts / Comments?