67N set to look towards source (could be generator or transformer) is relevant if there is another source in the same system that can feed the fault in the generator / transformer.Hi all,
When we have to use residual earth protection 51N and 67N and what's the difference?
Is it true that 67N is only used on the incomers and 51N on the outgoing feeders?
67N set to look towards source (could be generator or transformer) is relevant if there is another source in the same system that can feed the fault in the generator / transformer.
In case of simple distribution station such as a transformer connected to a busbar with number of outgoing feeders from the busbar, 67N has no relevance.
51N is used in all outgoing feeders as well as in the incomer. The 51N in the incomer acts as back up protection for outgoing feeder faults, while also being primary protection for faults in the busbar.
You seem to have no other incomers to the busbar other than those from the power plant. So, 51N in the incomers will be required as a back up protection for faults in the outgoing feeders. The other option in case this is to be disabled is the 51N at the upstream of the power plant incomers, if one exists there.The configuration we have is 2 incomers 1 & 2 (powered from the power plant) so two busbars with the ability to couple the two with a bus coupler breaker
Some outgoing feeders are connected on each incomer busbar. We had 51N protection on each incomer but the power plant asked to disable it and enable only 67N on each incomer, outgoing feeders still have 51N protection.
It has a thing related to protect their generator. Can you explain please how 67N in this case will work ?