rockman7892
- Apr 7, 2008
- 1,166
Can a residual CT connection or calculation in a relay be used to successfully detect and coordinate ground fault current on a MV LRG system? System is 2.4kV with resistance grounded secondary at 400A with a CT on the transformer neutral connected to relay in secondary switchgear main.
The feeders in this secondary 2.4kV Switchgear has 1200:5 phase CT's and does not have zero sequence CT's. I have always understood that zero sequence CT's were required for feeders on LRG systems in order for sensitive ground fault sensing (20A or so) Can the same level of sensitivity be achieved with the phase CT wired for a residual measurement or calculation?
With older electromechanical relays I know that you could not set the pickup low enough where high ratios were used for a residual connection (I believe .1 was lowest pickup settings for most electromechanical relays)however with the advent of electronic relays is this an issue anymore since you can set pickup as low as .02 in some relays?
On the contrary I know that you do not want to use zero sequence CT's on LRG systems due to saturation concerns.
Does the size of the CT on the transformer neutral typically match LRG rating i.e. 400A resistor uses 400:5 CT?