Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

Using Section I for Design & Construction of Heating Boilers.

Status
Not open for further replies.

IdanPV

Mechanical
Aug 26, 2019
425
0
16
IL
Hello all,

Is there any option (Code Case, Interpretation or Paragraph in the Code) which allow a Section I stamp holder to do Section IV jobs?
What I want to know if there any way that a manufactorer which have an "S (or E) stamp" will use his S stamp for Section IV jobs.
 
Replies continue below

Recommended for you

See ASME I, PG-2.2 below

ASME I
PG-2 SERVICE LIMITATIONS
PG-2.1 The rules of this Section are applicable to the following services:
(a) boilers in which steam or other vapor is generated at a pressure of more than 15 psig (100 kPa) for use external to itself
(b) high‐temperature water boilers intended for operation at pressures exceeding 160 psig (1.1 MPa) and/or
temperatures exceeding 250°F (120°C)

PG-2.2 For services below those specified in PG-2.1 it is intended that rules of Section IV apply; however, boilers for such services may be constructed and stamped in accordance with this Section provided all applicable requirements are met.

Regards - Juergen
 