Good article about this 2019 accident near Phoenix AZ in the IEEE Spectrum:
Dispute Erupts Over What Sparked an Explosive Li-ion Energy Storage Accident
The firefighters were severely injured by the explosion. The building was filled with explosive gas (hydrogen/HCN?) at the time thefirefighters opened the door, exposing the building's contaminated atmosphere to fresh oxygen, causing a deflagration.
My suspicion is that there was an emergency management plan, but that it predicted the fire suppression system to be effective. Since it wasn't, a large number of Lithium cells released gases, which were contained within the building. This left the firefighters with incorrect assumptions about what would happen the moment they opened the door.
Four Firefighters Injured In Lithium-Ion Battery Energy Storage System Explosion - Arizona
So the explosive gases were contained by the building. The flood of CO2 or HFC probably suppressed flames at first, but once the air in the building was consumed, the HCN gas continued to build.
Dispute Erupts Over What Sparked an Explosive Li-ion Energy Storage Accident
The firefighters were severely injured by the explosion. The building was filled with explosive gas (hydrogen/HCN?) at the time thefirefighters opened the door, exposing the building's contaminated atmosphere to fresh oxygen, causing a deflagration.
As thermal runaway moved through the rack, flammable gases continued to concentrate. Fire suppression devices were ineffective on the event.
My suspicion is that there was an emergency management plan, but that it predicted the fire suppression system to be effective. Since it wasn't, a large number of Lithium cells released gases, which were contained within the building. This left the firefighters with incorrect assumptions about what would happen the moment they opened the door.
Four Firefighters Injured In Lithium-Ion Battery Energy Storage System Explosion - Arizona
The design of the ESS did not include deflagration venting...
The total flooding clean agent suppression system prevented flaming during the early phase of the incident, but was not designed for and did not provide explosion protection.
So the explosive gases were contained by the building. The flood of CO2 or HFC probably suppressed flames at first, but once the air in the building was consumed, the HCN gas continued to build.