I've searched through the forum and found some close examples but for some reason my values are not coming out. Here is what is provided by the utility:
Primary Voltage = 24kV P to P
Fault Current LLL = 4863
Fault Current LG = 4364
X1/R1 = 9.62
X0/R0 = 4.56
My end goal is to develop the inputs for SKM which requires:
Three Phase Current and X/R
Line to Ground Current and X/R
The three phase current and X/R are a given since X/R in a three phase only has the positive sequence impedance X1/R1.
Line to Ground current is given so all I have to do is calculate SLG X/R ratio, this is giving me fits.
This is what I've done:
I3sc=4863<-84deg
Z1=Z2=Vll/(sqrt(3)*I3sc)
Z1=Z2=24kV/(1.73*4863<-84deg)
Z1= 0.2946+2.834j
Islg=4364<-77.63deg
Zg=3*Vln/Islg=3*13856<0/4364<-77.63deg
Zg=2.04042+9.304j
Z0=Zg-2*Z1
Z0= 1.45122+ 3.6362j
and finally, I thought at least
SLG X/R=(x0+2*x1)/(r0+2*r1)
SLG X/R=4.42
and as you can see I just calculated in a circle my original X0/R0 value!
Any direction in what I am messing up here?
Thanks in advance for any help here.
Primary Voltage = 24kV P to P
Fault Current LLL = 4863
Fault Current LG = 4364
X1/R1 = 9.62
X0/R0 = 4.56
My end goal is to develop the inputs for SKM which requires:
Three Phase Current and X/R
Line to Ground Current and X/R
The three phase current and X/R are a given since X/R in a three phase only has the positive sequence impedance X1/R1.
Line to Ground current is given so all I have to do is calculate SLG X/R ratio, this is giving me fits.
This is what I've done:
I3sc=4863<-84deg
Z1=Z2=Vll/(sqrt(3)*I3sc)
Z1=Z2=24kV/(1.73*4863<-84deg)
Z1= 0.2946+2.834j
Islg=4364<-77.63deg
Zg=3*Vln/Islg=3*13856<0/4364<-77.63deg
Zg=2.04042+9.304j
Z0=Zg-2*Z1
Z0= 1.45122+ 3.6362j
and finally, I thought at least
SLG X/R=(x0+2*x1)/(r0+2*r1)
SLG X/R=4.42
and as you can see I just calculated in a circle my original X0/R0 value!
Any direction in what I am messing up here?
Thanks in advance for any help here.