Working in a sugar factory in Texas. Utility is 13.2kv 3w+g. My switchgear utilizes sel 351 relays. It has a utility input, load breaker, tie breaker that connects another MV breaker to a transformer that has a 1000kw 480v transformer. The generator step up transformer is a 1000kva 13.2kv grounded wye : 480v delta.
A fault occurred on the utility side between C phase and ground. The utility breaker opened after 18 cycles and ALL of my MV breakers tripped and locked out only after 3 cycles. Only the main relay has voltage sensing.
Q1) How can all of my breakers trip and lockout?
Q2)can my system supply enough ground fault current? The secondary is open where is the source?
Q3) My gen transformer secondary is 480 delta and the gen breaker is opened how can ground fault current flow from the primary grounded wye to the utility fault?
Q4) Can 0 sequence current be pulled from the grounded wye and thus trip the feeder breaker? Would disconnecting the neutral to ground connection on the 13.2kv side prevent 0 sequence current from flowing? I still don't understand how it can flow if gen is not connected??
I hope these questions makes sense and I know I asked the same question a lot just hoping that it paints a better picture.
A fault occurred on the utility side between C phase and ground. The utility breaker opened after 18 cycles and ALL of my MV breakers tripped and locked out only after 3 cycles. Only the main relay has voltage sensing.
Q1) How can all of my breakers trip and lockout?
Q2)can my system supply enough ground fault current? The secondary is open where is the source?
Q3) My gen transformer secondary is 480 delta and the gen breaker is opened how can ground fault current flow from the primary grounded wye to the utility fault?
Q4) Can 0 sequence current be pulled from the grounded wye and thus trip the feeder breaker? Would disconnecting the neutral to ground connection on the 13.2kv side prevent 0 sequence current from flowing? I still don't understand how it can flow if gen is not connected??
I hope these questions makes sense and I know I asked the same question a lot just hoping that it paints a better picture.