Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

uv detector

Status
Not open for further replies.

islam jamal

Chemical
Oct 27, 2020
8
can i install UV Detector for Reformer methanol plant ?
 
Replies continue below

Recommended for you

The tubes in our methanol plant steam reformer ruptured because of overheating, and the investigation team recommended installation of UV flame detectors. I had bad experience with UV detectors in furnaces because they led to false alarms, trips and process disturbances. Can you please guide me on this issue?
 

I think the flames interference on uv sensors are the problem which can led to false readings, I don´t think that fixed uv sensors can be of an accurate help. Try to use skin thermocouples, well posicionated in several tubes points you consider more susceptible to more critical temperatures, and complement them, with an itenerant uv camera.

luis
 
A UV detector for a furnace, fired heater, or boiler is a flame detector; one part of a flame failure safety shutdown circuit. Its purpose is to shutdown the fuel supply when it detects loss of flame.

But, the flame safety circuit has nothing to do with temperature control, which if the problem was overheating, a flame safety component or system won't solve a temperature control problem.

I suspect that the investigation team is recommending flame safety because it's a safety issue. Apparently, there is no flame safety at the present?

To the question as to whether you can install a UV detector: the feasibility of retrofit to a burner involves compatibility of UV with the fuel (spectral response), mounting, sighting, wiring for power and signal, and the requisite flame safety controller and safety shutoff valves. There can be other sensor/switches providing interlocks in the flame safety system. Vendors that handle flame safety are usually pretty fluent in their application.
 