V/Hz Tripping Philosophy

Status
Not open for further replies.

veritas

Electrical
Oct 30, 2003
467
On a 780MVA steam turbine 23kV generator unit I wish to apply V/Hz protection (existing scheme being replaced and does not have this function currently). The X-protection V/Hz relay fed from a VT at the machine terminals whilst gen Y-relay VT connected to 23kV bus.

The IEEE Guide for AC Generator Protection recommends V/Hz tripping of the GCB and FCB only and only the FCB if machine offline.

What about loss of load condition? A load rejection scenario will most likely lead to an increase in both V and f thus weakening the efficacy of the V/Hz protection. I believe that overvoltage protection should step in here but am wandering if it is not safer to have a V/Hz condition result in a complete unit shutdown to prevent overexcitation damage of the unit trfr as well as generator?
 
Replies continue below

Recommended for you

Load rejection is dealt with by the overfrequeny relays and should have no impact on the V/Hz function.
 
If the V/Hz relationship is more-or-less maintained as the machine overspeeds from a load rejection then there shouldn't be any over-flux problem which is what the V/Hz relay is protecting you from. Plain over-voltage will trip the excitation if it simply gets too high. Normally the GSU and unit auxiliary transformers will run into problems long before the generator. A brief V/Hz excursion until the AVR gets control of the terminal voltage won't cause much harm to either the generator or the transformer.

If you have a load dump which causes a prolonged voltage excursion I suggest it would be better to trip the excitation to prevent an over-voltage or over-fluxing condition and leave the machine running, rather than to trip the unit overall. Better to have a controlled turbine shutdown than a trip any day.
 
All valuable comments, thank you. What I also have to bear in mind is that the OV, V/Hz, overfrequency protection, etc. need to co-ordinate with the AVR and governor control as these need to respond first for minor excursions of V and f.

Thanks again.
 
Kestrel Power Engineering ( has a program, GenCap, that provides the tools to verify coordination between various control responses and various protection functions. Quite powerful, if you want to take full advantage of it I would recommend one of their classes.
 