On a 780MVA steam turbine 23kV generator unit I wish to apply V/Hz protection (existing scheme being replaced and does not have this function currently). The X-protection V/Hz relay fed from a VT at the machine terminals whilst gen Y-relay VT connected to 23kV bus.
The IEEE Guide for AC Generator Protection recommends V/Hz tripping of the GCB and FCB only and only the FCB if machine offline.
What about loss of load condition? A load rejection scenario will most likely lead to an increase in both V and f thus weakening the efficacy of the V/Hz protection. I believe that overvoltage protection should step in here but am wandering if it is not safer to have a V/Hz condition result in a complete unit shutdown to prevent overexcitation damage of the unit trfr as well as generator?
The IEEE Guide for AC Generator Protection recommends V/Hz tripping of the GCB and FCB only and only the FCB if machine offline.
What about loss of load condition? A load rejection scenario will most likely lead to an increase in both V and f thus weakening the efficacy of the V/Hz protection. I believe that overvoltage protection should step in here but am wandering if it is not safer to have a V/Hz condition result in a complete unit shutdown to prevent overexcitation damage of the unit trfr as well as generator?