BigJohn1
Electrical
- May 24, 2003
- 57
Very unusual problem on a 25MVA transformer 34.5kV Y : 13.8kV Δ.
Has been in service for many years. Recent unexplained feeder fault blew a fuse. Now every single time the transformer is energized via the vacuum breaker it blows those same upstream feeder fuses. The transformer has so far always been energized unloaded.
After the initial fault, this sub was extensively tested:
[ul]
[li]Transformer PF, TTR, excitation, winding Ω, leakage X, and oil sampled.[/li]
[li]All bushings PF tested.[/li]
[li]All high and low side arrestors PF tested and AC overpotential.[/li]
[li]Breaker PF tested and resistance tested - No timing test yet.[/li]
[li]Overhead structure hipot.[/li]
[/ul]
No problems whatsoever. But every time the transformer is energized with any of the high side arrestors in place it blows fuses. Remove arrestors and re-energize and it stays energized. Add an arrestor and it blows a fuse on that phase.
Here's the kicker: All these affected arrestors are in the load-side of the VCB. There is an identical set of arrestors on the line side that have never blown any fuses: If the VCB is open the line side will remain happily energized for hours, as soon as the VCB closes, fuses pop.
I am at a lose except maybe to say that a new malfunction in the breaker is causing transformer overvoltage due to prestrike?
Any ideas at all?
Has been in service for many years. Recent unexplained feeder fault blew a fuse. Now every single time the transformer is energized via the vacuum breaker it blows those same upstream feeder fuses. The transformer has so far always been energized unloaded.
After the initial fault, this sub was extensively tested:
[ul]
[li]Transformer PF, TTR, excitation, winding Ω, leakage X, and oil sampled.[/li]
[li]All bushings PF tested.[/li]
[li]All high and low side arrestors PF tested and AC overpotential.[/li]
[li]Breaker PF tested and resistance tested - No timing test yet.[/li]
[li]Overhead structure hipot.[/li]
[/ul]
No problems whatsoever. But every time the transformer is energized with any of the high side arrestors in place it blows fuses. Remove arrestors and re-energize and it stays energized. Add an arrestor and it blows a fuse on that phase.
Here's the kicker: All these affected arrestors are in the load-side of the VCB. There is an identical set of arrestors on the line side that have never blown any fuses: If the VCB is open the line side will remain happily energized for hours, as soon as the VCB closes, fuses pop.
I am at a lose except maybe to say that a new malfunction in the breaker is causing transformer overvoltage due to prestrike?
Any ideas at all?