Validation of the inertia constant of a synchronous generator 3
Carlos Melim
24
Hello everybody,
I want to validate the inertia constant of a synchronous generator, stated by its supplier.
I have all the necessary instruments to study the behaviour of the generator including oscillo-perturbography recording devices.
I've read somewhere that one typical test is to perform a load reject of the generator by disconnecting it from the grid and studying the df/dt slope.
I need your help to decide the best testing procedure. I can perform load reject or load acceptance tests.
I think that if I choose a load acceptance test, the generator inertial response will depend on the response of all the other generators on the grid.
Am I right?
I am looking forward to hear your expert advices.
Best regards.
The problem is in the word 'generator'.
This implies that there is a 'prime mover' which provides mechanical power which the generator (ac or dc) turns into electrical power.
Unfortunately, prime movers are generally reciprocating internal combustion engines, which have friction, or turbines, steam, hydro or combustion gas types which have windage and / or hydraulic drag. This is looking at the system in very simplistic terms admittedly.
To determine the inertia constant, One first has to determine the inertia. Once the generator has been coupled on site to a prime mover, then this is difficult, if not impossible.
It can be done on works test, where the generator is tested on its own.
This is a real problem today since power network managers are finding that small scale generation (renewables etc) are becoming a larger portion of generation capacity as older thermal generation is retired. They then need to evaluate the inertia contribution of smaller generation, remembering that wind and solar power has little or no inertia contribution.
So there you are on site, with a gas turbine generator set, the manufacturer is out of business and no one knowsp the intertia of the shaft system.
So if anyone has a verifiable method of determining inertia on site, then I would be pleased to hear it, for my day job. I was asked this about a year ago, and our UK experts could not come up with a method!
It is a universal problem. Easy, if you go to the text-books where all secondary effects can be disregarded, but not so easy IRL. I have had problems doing the same thing on much simpler systems. Systems where I had a DC motor coupled to the inertia to be determined. And seldom systems above ten megawatts.
The main problem in such measurements is to find and compensate for windage, non-linear friction at low speeds and such things. If there are ball bearings, it can be done. With plain bearings, not so easy.
If you can disconnect the machine from the prime mover AND have access to a drive with at least 10% of the generators rated torque, it may be done. But it is not done in an hour or two. But if you have that and can couple the drive easily to the machine, then it can be done in one very long day. Or a couple of very long Days.
Assuming Square law windage and constant bearing friction, which is reasonable above a few RPM and below a few hundred RPM, then you can run a test at different speeds to get a grip on windage. Use that to compensate actual torque when you evaluate the main test later.
The main problem is to apply an external torque. The application of an external torque to a machine requires some ingenuity, sometimes there is a free shaft available at the NDE, but mostly not. Then a belt directly on the DE shaft may be a possibility. A flat belt has worked best in my tests. A timing belt doesn't slip but there are seldom such pulleys available on the machine under test.
Then, use the drive in constant torque mode, available on DC drives and most AC drives, and run an acceleration test. Compensate for windage and bearing friction with the data obtained in the first test and calculate the inertia from net torque and acceleration.
The second method is sometimes simpler and is based on the damped oscillation that a system executes when a step force is applied. Attach a lever to the shaft. That can usually be done with a clamp or using existing bolts. A clamp around the shaft is what I prefer. Then get a spring "with suitable strength and length" and affix it to the shaft and a fixed Point nearby. Stretch the spring with any suitable device and release quick so that energy is not lost by tearing the rope off. A wire cutter used to cut tug ropes may be necessary for fast release.
During this operation, record the shaft angle with a suitable transducer and calculate frequency from the damped oscillation. Once you have that, it is a standard class-room procedure to calculate inertia from the data.
I have used an inclinometer successfully to measure shaft position. It is easy to apply and produces a strong and linear signal that is easy to record with most devices. If there is low damping, high Q, the results will be as good as the spring constant measurement and length of arm measurements combined.
A Picture of a similar test (rotor resonance test) is shown in Picture below.
Gunnar Englund
Hi Carlos,
As others have said, validating the generator alone requires accelerating the generator alone. However your question on load rejection implies you want the total (generator+prime mover+coupling+etc.). In which case load rejection is the way to measure it, for the reason you have given (unless your machine is small enough that you can use a load bank with the machine isolated from external system). The machine speed variation is not (or should not be) great so windage and bearing friction are relatively constant. Rejections are stressful (on the machine and the observers) so it is prudent to start small and work up.
John.