IanVG
Mechanical
- Jan 21, 2022
- 73
I think I've got a good grasp on what valve authority is for individual circuits and how to apply it for designing & selecting AHU/FCU coil valves, but I cannot seem to find good guidance specifically for valve authority for variable primary and variable secondary systems. I got a full hydraulic model built out for a plant that delivers chilled water to six buildings. I am replacing the plant's chiller, and have several scenarios modeled out for various seasons and cooling demands. My question is how do I calculate the valve authority for the chiller inlet or outlet chilled water valve? I've got a total pressure drop across the system of 15.3 psi differential (psid), so using a valve authority of 50% (where I assume anywhere between 25% and 75% is acceptable), I would select a valve with a 100% open pressure drop of 7.65 psid. This means I am effectively increasing the pump head by 50%. Does good valve selection and valve authority apply differently for variable primary and variable secondary systems? I can upload sketches if necessary to clarify.