I'm working on a job that involves retrofitting NG gas blankets and vapor recovery units (VRUs) onto some existing tanks.
I have the flow rates and the fluid properties of the materials that I can run down to the tanks.
As backup for the VRUs, the tanks will be equipped with vacuum/breather valves sized per API 2000.
The question I have is wrt the VRUs. The tanks vary in size from 25,000 to 150,000 bbls. Maximum flow rate to each tank is about the same and the estimation of the displaced vapor flow rate to the VRU is straight forward. However, the thermal outbreathing requirements are substantial and are significant greater (up to 7 times greater for the largest tank) than the gas displaced by liquid movement into the tank. I’ve talked to the VRU vendor we are likely going to go with as well as the tank breather valve technical group (this person also has a good knowledge of VRUs).
The VRU vendor has quite a few units in operation and in some cases, the customer has sized the units and in other cases they have sized the units. They size the units on the basis of the gas displaced by the incoming liquid and do not include the thermal outbreathing requirement, their customers have used the same basis. None of their units have had a problem with meeting capacity and not venting excess gas to the atmosphere through the vent valves. They recognize the discrepancy but believe the fact their units do not vent suggests the API 2000 thermal outbreathing flow rates are very conservative. The person I talked to at the tank breather valve company said that in his experience, some companies do include the thermal outbreathing requirements in the VRU capacity basis but this is a company practice as opposed to a process or fluid property that might result in higher capacity requirements.
For example, a 150,000 bbl tank in high flash point service (greater than 100F) requires a thermal outbreathing capacity of 47,500 scfh. This is equivalent to raising the internal temperature of the gas, assuming the tank was intially empty, by about 30F which seems high to me to actually achieve. The tanks will normally contain product which will be above ambient temperature and I was wondering if this might moderate the internal pad gas temperature such that the API 2000 thermal outbreathing requirements are effectively ‘smoothed’ out.
I’d appreciate any comments/experience others have. Sorry for the long post.
I have the flow rates and the fluid properties of the materials that I can run down to the tanks.
As backup for the VRUs, the tanks will be equipped with vacuum/breather valves sized per API 2000.
The question I have is wrt the VRUs. The tanks vary in size from 25,000 to 150,000 bbls. Maximum flow rate to each tank is about the same and the estimation of the displaced vapor flow rate to the VRU is straight forward. However, the thermal outbreathing requirements are substantial and are significant greater (up to 7 times greater for the largest tank) than the gas displaced by liquid movement into the tank. I’ve talked to the VRU vendor we are likely going to go with as well as the tank breather valve technical group (this person also has a good knowledge of VRUs).
The VRU vendor has quite a few units in operation and in some cases, the customer has sized the units and in other cases they have sized the units. They size the units on the basis of the gas displaced by the incoming liquid and do not include the thermal outbreathing requirement, their customers have used the same basis. None of their units have had a problem with meeting capacity and not venting excess gas to the atmosphere through the vent valves. They recognize the discrepancy but believe the fact their units do not vent suggests the API 2000 thermal outbreathing flow rates are very conservative. The person I talked to at the tank breather valve company said that in his experience, some companies do include the thermal outbreathing requirements in the VRU capacity basis but this is a company practice as opposed to a process or fluid property that might result in higher capacity requirements.
For example, a 150,000 bbl tank in high flash point service (greater than 100F) requires a thermal outbreathing capacity of 47,500 scfh. This is equivalent to raising the internal temperature of the gas, assuming the tank was intially empty, by about 30F which seems high to me to actually achieve. The tanks will normally contain product which will be above ambient temperature and I was wondering if this might moderate the internal pad gas temperature such that the API 2000 thermal outbreathing requirements are effectively ‘smoothed’ out.
I’d appreciate any comments/experience others have. Sorry for the long post.