Jon_Doe
Electrical
- Mar 30, 2023
- 11
Hi there everyone.
I know variable speed compressors can be overdriven and also run very low.
Some sources indicate down to 10% but most it's no less than 30%.
What i could not really find out is data about efficiency of the system at very low speeds.
The reason i'm pondering this is that i have a situation with a rather well insulated envelope, where peak required power in the worst possible time of year would be ~3.5kW - 12kBTU - 1ton.
That time may be 3% of the year and only on some odd years.
However, most of the time, the required power would be way below this value, like 10%-30%.
Commercial, off the shelf, inverter air to water heat pumps are at least twice this much and would need to run at the lowest setting, and even cycle on/off like a fixed speed unit, negating some of the advantages of variable speed.
So, how would a large compressor run at minimum speed compare, from efficiency point of view, to another one, half it's size, at a medium speed ?
There may be a remote possibility of repurposing a standard mini-split, very efficient, 12KBTU inverter AC to do this but it requires some surgery.
That may not be such a problem but warranty voiding may.
Any thoughts ?
I know variable speed compressors can be overdriven and also run very low.
Some sources indicate down to 10% but most it's no less than 30%.
What i could not really find out is data about efficiency of the system at very low speeds.
The reason i'm pondering this is that i have a situation with a rather well insulated envelope, where peak required power in the worst possible time of year would be ~3.5kW - 12kBTU - 1ton.
That time may be 3% of the year and only on some odd years.
However, most of the time, the required power would be way below this value, like 10%-30%.
Commercial, off the shelf, inverter air to water heat pumps are at least twice this much and would need to run at the lowest setting, and even cycle on/off like a fixed speed unit, negating some of the advantages of variable speed.
So, how would a large compressor run at minimum speed compare, from efficiency point of view, to another one, half it's size, at a medium speed ?
There may be a remote possibility of repurposing a standard mini-split, very efficient, 12KBTU inverter AC to do this but it requires some surgery.
That may not be such a problem but warranty voiding may.
Any thoughts ?