DuctHunter
Mechanical
- Aug 14, 2007
- 31
What sequence of operation is best to use on the VAV box when you have a reheat coil.
One company I worked for had it customary to have the VAV box in maximum airflow setting when needing heating from the reheat coil. They would size the reheat coil based on the VAV box maximum airflow rate. Other engineers I talk to size the reheat coil for the VAV box minimum air flow setting. So on call for heat the VAV box goes to the minimum airflow setting and the slowly ramps up as more heat is needed.
The logic behind keeping the box airflow at the maximum is because when heating the air, if you cut the air to the minimum the velocity will be so low that the heated air will never drop down and will just stay near the ceiling.
I'd like to know what sequence others use and what airflow rate is the reheat coil sized for.
Thanks for your input.
One company I worked for had it customary to have the VAV box in maximum airflow setting when needing heating from the reheat coil. They would size the reheat coil based on the VAV box maximum airflow rate. Other engineers I talk to size the reheat coil for the VAV box minimum air flow setting. So on call for heat the VAV box goes to the minimum airflow setting and the slowly ramps up as more heat is needed.
The logic behind keeping the box airflow at the maximum is because when heating the air, if you cut the air to the minimum the velocity will be so low that the heated air will never drop down and will just stay near the ceiling.
I'd like to know what sequence others use and what airflow rate is the reheat coil sized for.
Thanks for your input.